液化石油气瓶煤气瓶使用问题

餐饮场所厨房内使用瓶装液化石油气等燃气瓶供气时,瓶数量有要求吗?

逆行无疆 | 2022-07-13 10:48
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

周家斌 2022-07-13 14:23 11 [回复]举报

参考江苏省和陕西省有地方文件规定:例如关于发布《餐饮场所使用燃气基本安全要求》的公告 http://zjj.weinan.gov.cn/ggbw/ywgz/65510.htm

液化石油气瓶总重量超过100 千克(折合2瓶50千克或7瓶15千克气瓶)

消防黄河 2022-07-14 09:47 00 [回复]举报

严禁使用。

消防黄河 2022-07-14 09:47 20 [回复]举报

燃气工程项目规范》为国家标准,编号为GB55009-2021,自2022年1月1日起实施。6.2.3(强制性条文) 公共用餐区域、大中型商店建筑内的厨房不应设置液化天然气气瓶、压缩天然气气瓶及液化石油气气瓶。

逆行无疆   回复: 消防黄河2022-07-14 12:45

大中型商店有定量标准吗?

0    0 [回复]举报

消防黄河   回复: 消防黄河2022-07-14 21:49

商店建筑设计规范

0    0 [回复]举报

周家斌   回复: 消防黄河2022-07-15 08:39

公共用餐区域和餐饮厨房是两个场区。两个概念。

0    0 [回复]举报

消防黄河 2022-07-14 21:48 00 [回复]举报

商店建筑设计规范1.0.4