直灌式加压送风系统安装在楼梯间内可以吗

有个项目原有正压送风风机直接放在3层楼梯间内,这样可以吗?

消防网友62117 | 2023-11-20 12:04
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

安洪全 2023-11-20 13:18 00 [回复]举报

建筑防烟排烟系统技术标准 GB51251-2017


3.3.3 建筑高度小于或等于50m的建筑,当楼梯间设置加压送风井(管)道确有困难时,楼梯间可采用直灌式加压送风系统,并应符合下列规定:    


1 建筑高度大于32m的高层建筑,应采用楼梯间两点部位送风的方式,送风口之间距离不宜小于建筑高度的1/2 ;     

2 送风量应按计算值或本标准第3.4.2条规定的送风量增加20%;     


3 加压送风口不宜设在影响人员疏散的部位。

阳明心 2023-11-21 09:51 00 [回复]举报

楼梯间内怎么能放风机呢???

whale 2023-11-21 10:39 00 [回复]举报

不行啊,风机要放在专用的机房内,不能直接放楼梯间内

whale   回复: whale2023-11-21 10:45

建筑防烟排烟系统技术标准 GB51251-2017没执行前风机可以不设置在机房内,保证风机下高度的话是可以的。

2    0 [回复]举报