26层北连廊住宅连廊位置防火门设置在这个位置是否符合规定?连廊连接处是否需要安装防火门?

雪国的岛村 | 2024-12-16 15:23
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

同同不同 2024-12-16 22:54 10 [回复]举报

看不太清,入户门是乙级门的话也行

雪国的岛村 2024-12-17 09:30 00 [回复]举报

我放了一张更清晰点的图,图上可能只是方案的图,没标的那么详细,实际建出来以后如问题中的一样在圈的位置加了防火门,我看过其他项目一般都是加在连廊位置的吧

LHH2737   回复: 雪国的岛村2024-12-17 09:55

加在连廊的两端

0    0 [回复]举报

雪国的岛村   回复: LHH27372024-12-17 12:33

那请问下,现在建设完后,防火门是加在入户位置,这合规吗?

0    0 [回复]举报

wetom 2024-12-17 14:55 00 [回复]举报

个人理解,仅供参考。

1、目前的做法没问题。户门为乙级防火门或者走道增加防火门,将户门与前室分隔,两种做法都可以。

2、连廊处可以安装普通门、防火门,也可以不安装门,按你的图连廊处不能安装门了,否则前室的防烟没办法解决。连廊要安装门的话,陕西这边要求可双向开启的门。

shijieyang40 2024-12-17 15:04 00 [回复]举报

当住宅建筑的 2 个安全出口(疏散楼梯)分散设置距离不小于5m且敞廊长度不小于4m时,之间连通的敞廊上可不设防火门,可不按照三合一前室考虑。

jinyanwu 2024-12-17 17:15 00 [回复]举报

个人意见,仅供参考:

从图上看,仅仅从防火的角度来说,应该可以。

无非就是增加了你的户内面积,只要周围邻居和物业不说就行。

图上正中间连廊处属于开敞空间,本来就是露天的,设置防火门应该没有意义。