消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

楼梯间和前室能共同一台风机吗?见哪条规范?

楼梯间和前室能共同一台风机吗?见哪条规范?

易学 | 2025-01-09 10:13
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

阳明心 2025-01-09 12:25 10 [回复]举报

《建筑防烟排烟系统技术标准》

3.1.5 防烟楼梯间及其前室的机械加压送风系统的设置应符合下列规定:
1 建筑高度小于或等于50m的公共建筑、工业建筑和建筑高度小于或等于100m的住宅建筑,当采用独立前室且其仅有一个门与走道或房间相通时,可仅在楼梯间设置机械加压送风系统;当独立前室有多个门时,楼梯间、独立前室应分别独立设置机械加压送风系统。
2 当采用合用前室时,楼梯间、合用前室应分别独立设置机械加压送风系统
3 当采用剪刀楼梯时,其两个楼梯间及其前室的机械加压送风系统应分别独立设置

潘天坤 2025-01-09 13:20 00 [回复]举报

请问是独立前室有几个门?是剪刀楼梯嘛?是前室还是合用前室呢?

当独立前室有多个门时,楼梯间、独立前室应分别独立设置机械加压送风系统

对于采用合用前室的防烟楼梯间,当楼梯间和前室均设置机械加压送风系统时,楼梯间、合用前室的机械加压送风系统应分别独立设置(当为与其他楼梯间或消防电梯不合用前室的防烟楼梯间,且楼梯间和前室均设置机械加压送风系统时,楼梯间与前室的机械加压送风系统一般应分别独立设置 。 本条虽然未做强制要求,但如果不分别独立设置送风系统,则必须采取可靠的风量调节措施确保楼梯间与前室之间的压差符合设计和本规范第 11.2.5 条的要求)

对于在梯段之间采用防火隔墙隔开的剪刀楼梯间,当楼梯间和前室(包括共用前室和合用前室)均设置机械加压送风系统时,每个楼梯间、共用前室或合用前室的机械加压送风系统均应分别独立设置(当剪刀楼梯间的两个前室均各自独立,不相互共用,也不与消防电梯前室合用时,每个楼梯间及其前室的机械加压送风系统应分别独立设置,同一个楼梯间与其前室的加压送风系统可以不独立设置,但应满足相应的压差要求;当剪刀楼梯间的两个前室共用,或任一前室与消防电梯前室合用,或共用前室与消防电梯前室合用时,每个楼梯间的机械加压送风系统均应与共用前室或合用前室的机械加压送风系统分别独立设置;其中不与消防电梯前室合用,也不与其他楼梯间前室共用的前室,可以与相应楼梯间的加压送风系统合用同一个系统,但应满足相应的压差要求)

对于建筑高度大于100米的建筑中的防烟楼梯间及其前室,其机械加压送风系统应竖向分段独立设置,且每段的系统服务高度不应大于100米

备注:独立设置是指楼梯间的加压送风系统与前室(包括共用前室、合用前室)的加压送风系统完全独立、互 不影响,系统的送风口、送风管道、送风机和控制阀等分别独立设置,不共用



通风设备 2025-01-15 12:01 00 [回复]举报

不能,要独立设置

关闭

关闭

手机APP下载