消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

室外消火栓设计流量取值问题

现接收到一项目,主体为乙类仓库,建筑设计体积>20000m³,但是GB 50974-2014中3.3.2中室外消火栓设计流量为“-”,这种情况建筑方案设计是否为不可取,一位置甲乙类仓库体积是否就不可以大于20000m³?

画图匠 | 2021-05-27 16:07
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

刘丽波 2021-05-27 17:00 00 [回复]举报

画图匠   回复: 刘丽波2021-06-02 11:50

谢谢。给规范编委组打过电话,编委专家说后期规范可能要与时更新,现可按建筑体积的递增,等差增大室外消防设计流量。但当地给审图中心沟通时,审图专家说没有规范依据,否定了甲乙类建筑体积超2W的方案。

0    0 [回复]举报

关闭

关闭

手机APP下载