消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

负二层食堂餐厅,楼梯共用问题

有个项目,两层地下室,负二层有个员工食堂和厨房,在负二层的时候独立防火分区,楼梯独立,不和车库共用,但是到了负一层又变成了车库的疏散梯,这样设计是否有问题,一直找不到相应的规范支持。

清辉雨 | 2022-03-23 17:29
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 6

石小东 2022-03-23 23:50 10 [回复]举报

汽车库、修车库、停车场设计防火规范中要求安全出口独立,楼梯间防烟。你们这个情况只要符合安全出口对立,防烟是可以的啊,没问题。

月半猫 2022-03-24 10:21 10 [回复]举报

负二层楼梯入口处,独立的防烟前室,负一层入口处,也有防烟前室,并没有问题啊。

清辉雨   回复: 月半猫2022-03-24 18:33

主要是怕疏散口上下串用了,上下功能不同

0    0 [回复]举报

清辉雨   回复: 清辉雨2022-05-28 16:33

审查没问题。可以这样做。

0    0 [回复]举报

9527 2022-03-24 15:03 10 [回复]举报

个人感觉确实支持不了。

首先,感觉现场情况应该是:汽车库和食堂所在建筑A应该属于2个单体建筑,贴邻建造。共用楼梯间也应该是在同一单体建筑的不同防火分区之间。

然后,公建A的食堂所在防火分区设计疏散宽度并未计算车库人员疏散需求。

其次,规范满足一定条件,允许汽车库借用住宅部分的疏散楼梯,并未允许借用公共建筑楼梯。

最后,即使汽车库和食堂属于同一单体建筑,食堂偏向于人员密集场所,或者就是人员密集场所,二者应该采取更为严格的分隔方式,还是不宜竖向共用疏散楼梯。

清辉雨   回复: 95272022-03-24 18:20

嗯,我也是偏向你的看法,下个月送审看下具体审查师如何理解。

0    0 [回复]举报

关闭

关闭

手机APP下载