小商铺疏散照明怎么考虑

有一个商业步行街,全是2、3层小单体,各单体建筑面积大的400平小的就80平(2层),室外楼梯,每个单体里面几个小商铺,30平左右,这种疏散照明怎么考虑;

逗你玩儿 | 2022-06-07 11:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

牛疼 2022-06-14 11:54 00 [回复]举报

人员密集场所消防安全管理 GB/T40248-2021 8.3.4 营业厅内的疏散指示标志设置应符合下列要求:     a)应在疏散通道转弯和交叉部位两侧的墙面、柱面距地面高度1.0m以下设置灯光疏散指示标志;有困难时,可设置在疏散通道上方2.2m~3.0m处;疏散指示标志的间距不应大于20m;    b)灯光疏散指示标志的规格不应小于0.5m×0.25m;    c)总建筑面积大于5000㎡的商场或建筑面积大于500㎡的地下或半地下商店,疏散通道的地面上应设置视觉连续的灯光或蓄光疏散指示标志;其他商场,宜设置灯光或蓄光疏散指示标志。

商店建筑电气设计规范 JGJ392-2016 5.3.1 商店建筑的下列部位应设置疏散照明:     1 封闭楼梯间、防烟楼梯间及其前室、消防电梯间的前室或合用前室、避难走道、避难层(间)、疏散走道。     2 建筑面积大于200㎡的营业区域。     3 建筑面积大于100㎡的地下或半地下商店。

建筑设计防火规范 GB50016-2014(2018年版)10.3.1 除建筑高度小于27m的住宅建筑外,民用建筑、厂房和丙类仓库的下列部位应设置疏散照明:     1 封闭楼梯间、防烟楼梯间及其前室、消防电梯间的前室或合用前室、避难走道、避难层(间);     2 观众厅、展览厅、多功能厅和建筑面积大于200m²的营业厅、餐厅、演播室等人员密集的场所;     3 建筑面积大于100m²的地下或半地下公共活动场所;     4 公共建筑内的疏散走道;     5 人员密集的厂房内的生产场所及疏散走道。

建议设置独立的蓄电式应急照明、疏散指示、安全出口灯,施工方便且满足现场需求。

逗你玩儿   回复: 牛疼2022-08-04 19:16

看了您的建议,是否设置应急照明配电箱,或者是从商铺配电箱接引,A型灯具如何从商铺配电箱取电,是不是设置降压装置,室外楼梯灯具是否也从商铺接引

0    0 [回复]举报

牛疼   回复: 逗你玩儿2022-08-05 09:34

建议将公共区域与商户进行区分;

公共区域(疏散通道、楼梯等)统一划分为一个控制系统;

商铺内根据体量确定是否采用集中控制型或非集中控制型,具体灯具的选型根据现场情况修改;如采用从户内取电,建议更换为B型灯具。

1    0 [回复]举报