消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

丙类仓库帖邻设置办公楼

丙类仓库帖邻设置办公楼,采用防火墙隔断,可以吗,有没有规范要求

曹树杰 | 2022-10-28 10:13
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

逍遥仙 2022-10-28 16:08 10 [回复]举报

丙类仓库与办公楼不能贴临设置,按 建筑设计防火规范 GB50016-2014(2018年版)3.5.2条规定,只有丁戊类仓库与民用建筑防火间距可放宽,见3.5.3条规定。如果是办公室可设置在仓库内满足3.3.5规定即可。

南明离火   回复: 逍遥仙2022-10-29 10:00

参照3.5.2 注2 ……占地面积不大于一座仓库的最大允许占地面积,防火间距也可以不限,丙类也适用这种情况

0    0 [回复]举报

逍遥仙   回复: 南明离火2022-10-29 13:13

3.5.2注2针对的都是仓库之间。工业建筑中只有丙丁戊厂房和丁戊仓库,其与民用建筑可以放宽,并且条件相对严苛,可详细阅读建规有关厂房和仓库防火间距有关条文。

0    0 [回复]举报

关闭

关闭

手机APP下载