消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

直通室外的配电间的门要采用防火门吗

直通室外的配电间的门要采用甲级防火门吗

消防砖家 | 2022-11-01 10:13
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

永锅 2022-11-01 10:24 00 [回复]举报

变配电室开向建筑内的门应采用甲级防火门,直通室外的门无要求。

周家斌 2022-11-01 10:28 00 [回复]举报

要具体看配电房的位置,与相邻和相对建筑物的防火间距情况,是需要防火门的。

消防砖家   回复: 周家斌2022-11-09 16:59

如果是配电间,配电间的门直通室外,是否可以采用普通门

0    0 [回复]举报

周家斌   回复: 消防砖家2022-11-10 10:47

一般是可以不用防火门,要看具体位置的,如果与有防火分区外墙相邻洞口距离不够的情况下,还是要防火门的,

0    0 [回复]举报

xie00   回复: 消防砖家2024-08-28 14:42

配电间外开的门必须防火门,不过等级根据各种规范要不同要求,

《20kV及以下变电所设计规范》 GB50053-2013 >6.1.3(黑体强条),直通室外的应为丙级防火门

民用建筑电气设计标准 GB51348-2019 >第4.10.3(非强条),当变电所设置在建筑首层,且向室外开门的上层有窗或非实体墙时,变电所直接通向室外的门应为丙级防火门,变电所位于多层建筑物的首层时,通向相邻房间或过道的门应为乙级防火门。(这条理解有点乱,如果门上层时实体墙,那么按乙级?)

民用建筑设计统一标准 GB50352-2019 >8.3.2(非强条)要求直通室外的不低于丙级防火门,除了这个其他必须甲级



0    0 [回复]举报

关闭

关闭

手机APP下载