前室送风系统,系统风量为48000m3/h,其楼层送风量多大。

前室送风系统,楼梯和前室分别设置送风,前室系统风量为48000m3/h,其楼层层数为5层,其每一层送风量分别为多少,如何计算得出。

殇~~ | 2022-12-02 14:08
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

张牙舞爪的张 2022-12-02 17:50 00 [回复]举报

个人认为:按一栋建筑只发生一起火灾计算。楼层中其中一层着火(一层一个防火分区),该楼层及上下两层前室常闭送风口开启,送风机启动。则每层前室送风量最少为1600m³,最大为2400m³。注:如果按验收标准,上述送风量可有10%的偏差。

消防网友68723 2022-12-05 11:03 00 [回复]举报

依据3.1.2 建筑高度大于50m的公共建筑、工业建筑和建筑高度大于100m的住宅建筑,其防烟楼梯间、独立前室、共用前室、合用前室及消防电梯前室应采用机械加压送风系统。 3.1.3 建筑高度小于或等于50m的公共建筑、工业建筑和建筑高度小于或等于100m的住宅建筑,其防烟楼梯间、独立前室、共用前室、合用前室(除共用前室与消防电梯前室合用外)及消防电梯前室应采用自然通风系统;当不能设置自然通风系统时,应采用机械加压送风系统,5.1.3 当防火分区内火灾确认后,应能在15s内联动开启常闭加压送风口和加压送风机。并应符合下列规定:     1 应开启该防火分区楼梯间的全部加压送风机;     2 应开启该防火分区内着火层及其相邻上下层前室及合用前室的常闭送风口,同时开启加压送风机。

mshm 2023-12-21 17:14 00 [回复]举报

简单点的除以3