汽车库采用预作用系统,喷头能参考厂房采用标准响应型扩大覆盖面积喷头吗?

汽车库采用预作用系统,喷头能参考厂房采用标准响应型扩大覆盖面积喷头吗?

mshm | 2023-01-07 10:03
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

张牙舞爪的张 2023-01-07 16:35 00 [回复]举报

汽车库采用预作用喷水灭火系统前提是满足《GB50067》7.2.2。根据《喷规》规定,汽车库属于中危险二级场所。如果我没记错的前提,采用扩大覆盖面积洒水喷头,对高度要求不大于8米即可。

Hydrant 2023-01-17 16:06 00 [回复]举报

《喷规》6.1.1,扩大覆盖面积喷头需要快速响应喷头;6.1.7条又规定,当采用快速响应洒水喷头时,系统应为湿式系统。另外再根据6.1.1的条文解释,预作用系统也是不应该用扩大覆盖面积喷头的。