水喷雾灭火系统采用电动控制和手动控制打开雨淋阀,电动控制按钮和手动控制球阀是否许安装在防护区内,有没有规范依据

水喷雾灭火系统采用电动控制和手动控制打开雨淋阀,电动控制按钮和手动控制球阀是否许安装在防护区内,有没有规范依据

消防砖家 | 2023-03-15 08:42
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

永锅 2023-03-15 09:07 00 [回复]举报

《水喷雾灭火系统技术规范》GB 50219-2014

5.3.2 雨淋报警阀、电动控制阀、气动控制阀宜布置在靠近保护对象并便于人员安全操作的位置。

陈曲 2023-03-15 12:06 00 [回复]举报

防护区内你要考虑的是万一情况下 谁进去操作 

消防网友72588 2023-03-18 00:07 00 [回复]举报

雨淋阀启动的电磁阀一般是由①报警系统自动启动、消控室切换手动控制远程启动②报警阀间手动球阀现场开启启动。

有些项目想加远程启动按钮,但是远程按钮启动不能与自动报警系统共用电磁阀,否则会造成故障。最简单的方法就是将原有电磁阀和手动启动球阀连接的三通换成四通,加装一个电磁阀,专门用于远程手动启动按钮。

个人经验,无规范及依据,有知道的大佬可以分享下。