风管多长时加内支撑

通风管道多长时加内支撑,有压的风管加,无压的不加

请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

同同不同 2023-06-20 21:16 00 [回复]举报

通风管道技术规程 JGJ/T141-2017      3.2.7 风管加固应符合下列规定:     1 薄钢板法兰风管宜轧制加强筋,加强筋的凸出部分应位于风管外表面,排列间隔应均匀,板面不应有明显的变形。     2 风管的法兰强度低于规定强度时,可采用外加固框和管内支撑进行加固,加固件距风管连接法兰一端的距离不应大于250mm。     3 外加固的型材高度应等于或小于风管法兰高度,且间隔应均匀对称,与风管的连接应牢固,螺栓或铆接点的间距不应大于220mm;外加固框的四角处,应连接为一体。     4 风管内支撑加固的排列应整齐、间距应均匀对称,应在支撑件两端的风管受力(压)面处设置专用垫圈。采用管套内支撑时,长度应与风管边长相等。     5 直缝圆形风管的直径大于或等于800mm且管段长度大于1250mm或总表面积大于4㎡时,可采用法兰形式加固。     6 矩形风管刚度等级及加固间距宜按本规程表3.1.5-1、表3.2.7-1~表3.2.7-4进行选择和确定。

潘天坤 2024-06-24 18:35 00 [回复]举报

达到一定要求的风管(不是所有规格都需要加固),当采用内支撑加固方式时(可以采用其他加固方式),才需要设置内支撑加固。采用内支撑加固的时候,可以参照通风管道技术规程 JGJ/T141-2017

通风与空调工程施工质量验收规范 GB50243-2016第4.2.3.3条规定: 
金属风管的加固应符合下列规定:2) 矩形风管的边长大于630mm,或矩形保温风管边长大于800mm,管段长度大于1250mm;或低压风管单边平面面积大于1.2㎡,中、高压风管大于1.0㎡,均应有加固措施
长边尺寸为2000毫米的排烟风管,如果是金属矩形风管,需要设置加固措施,常见加固方式为楞筋加固及内支撑加固。有单楞筋加固的,也有楞筋加固结合内支撑加固,个人觉得楞筋加固结合内支撑加固方式稳定性比较好。
通风与空调工程施工质量验收规范 GB50243-2016第4.3.1.3条规定:
金属风管的加固应符合下列规定:1) 风管的加固可采用角钢加固、立咬口加固、楞筋加固、扁钢内支撑、螺杆内支撑和钢管内支撑等多种形式(图4.3.1);5) 当中压、高压系统风管管段长度大于1250mm时,应采取加固框补强措施。高压系统风管的单咬口缝,还应采取防止咬口缝胀裂的加固或补强措施。
至于加固框补强措施针对每节风管还是整段风管,有一些争议,这边不展开说