哪些情况消火栓箱内可以不带消防软管卷盘

哪些情况消火栓箱内可以不带消防软管卷盘

666125 | 2023-06-25 11:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

安洪全 2023-06-25 11:25 00 [回复]举报

可不设:

消防给水及消火栓系统技术规范 GB50974-2014

7.1.4 建筑高度不大于27m的多层住宅建筑设置室内湿式消火栓系统确有困难时,可设置干式消防竖管。



除了应设的场所或建筑外,其余可不设,下列为应设的场所

建筑设计防火规范 GB50016-2014(2018年版)

8.2.4 人员密集的公共建筑、建筑高度大于100m的建筑和建筑面积大于200m²的商业服务网点内应设置消防软管卷盘或轻便消防水龙。高层住宅建筑的户内宜配置轻便消防水龙。

老年人照料设施内应设置与室内供水系统直接连接的消防软管卷盘,消防软管卷盘的设置间距不应大于30.0m。


建筑防火通用规范 GB55037-2022

7.1.15 避难层、间应设:

3 避难层应设置消防电梯出口、消火栓、消防软管卷盘、灭火器、消防专线电话和应急广播。

宋奇 2023-06-25 11:32 00 [回复]举报

楼上的,问题是软管卷盘什么情况不安装?

参考这个条文,剩下的情况就不用装了:

8.2.4 人员密集的公共建筑、建筑高度大于100m的建筑和建筑面积大于200m²的商业服务网点内应设置消防软管卷盘或轻便消防水龙。高层住宅建筑的户内宜配置轻便消防水龙。
    老年人照料设施内应设置与室内供水系统直接连接的消防软管卷盘,消防软管卷盘的设置间距不应大于30.0m。

大树119 2023-07-02 07:09 00 [回复]举报

除了人密,老照,超高层和大于两百平的商业服务网点,其余都可以不设