甲类多层厂房,二层有甲类生产车间,那原材料可以在二层做临时堆放吗?

此种情况,适合定义成中间仓库吗?

如果不放在二层,每次来材料都要外运进来,也不现实。

张先生2024 | 2024-02-03 12:04
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

13029082207 2024-04-01 13:25 00 [回复]举报

看你是否符合中间仓库 的条件了

是不是靠外墙存储   不超过1昼夜的量   是否用防火墙+1.5小时楼板分隔 、

参照规范

建筑设计防火规范 GB50016-2014(2018年版)


3.3.6 厂房内设置中间仓库时,应符合下列规定:
1 甲、乙类中间仓库应靠外墙布置,其储量不宜超过1昼夜的需要量;
2 甲、乙、丙类中间仓库应采用防火墙和耐火极限不低于1.50h的不燃性楼板与其他部位分隔;
3 丁、戊类中间仓库应采用耐火极限不低于2.00h的防火隔墙和1.00h的楼板与其他部位分隔;