台球厅包厢疏散

下边包厢甲方要求装门,这样会不会不符合防火通用规范7.1.2的规定?还是说库房是人员不经常停留房间,也是可以的?

酸奶不酸 | 2024-06-27 12:17
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

LHH2737 2024-06-27 13:55 00 [回复]举报

符合,这不属于房间疏散门

倜圳 2024-06-27 14:15 00 [回复]举报

可以装

无名之辈 2024-06-27 15:47 00 [回复]举报

主要是二级嵌套的问题有争议,建议事先和图审审查师沟通一下为妥。

phone0224 2024-06-27 16:51 00 [回复]举报

可以这么设置,但是要注意下面这个包厢的面积要包括库房的面积来判定这个房间是否需要设置几个疏散门,另外,最远点的疏散距离也要从库房内最远点开始算,看看是否符合规范要求。