消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防设计审查

对现有的劳动密集型企业的员工宿舍(总建筑面积约4000㎡)加装火灾自动报警系统(如烟感+加入到现有的联动报警主机中),需要专门的消防设计单位出设计方案图纸吗?需要进行消防设计审查吗?

消防网友34946 | 2024-07-10 17:06
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0

回答 | 7

LHH2737 2024-07-11 09:20 00 [回复]举报

没有改变使用功能和使用单位可以审查,但建议找设计单位按规范出图

老刘头 2024-07-11 18:55 00 [回复]举报

原有合法投入使用建筑从整改火灾隐患角度,只需要消防设计,可以不需要消防设计审查。在竣工后需报请消防救援机构进行检查。如果建筑没有合法性,那需要按照建设工程改造中特殊建设工程的规定到当地住建部门依法办理消防审验手续,不仅需要设计、审图、还有正规的施工、竣工验收。

消防网友34946   回复: 老刘头2024-07-15 14:05

只需要消防设计,不需要审查,验收报消防机构检查(抽查?)是有什么相关的出处吗?


按照《建设工程消防设计审查验收管理暂行规定》第十四条规定,该员工宿舍总建筑面积4000平方米,属于特殊建设工程,需要进行消防设计审查的。

0    0 [回复]举报

老刘头   回复: 消防网友349462024-07-15 20:49

该建筑按规范规定不需要设置火灾自动报警系统,单位从自身加强管理的角度增设的火灾自动报警系统,不需要到住建办理审批手续,不需要设计审查。

0    0 [回复]举报

老刘头 2024-07-11 19:01 00 [回复]举报

员工宿舍为什么要设置火灾自动报警系统?

逆游的魚 2024-07-11 19:59 00 [回复]举报

需要

811 2024-07-26 00:42 00 [回复]举报

 是的  需要设计可私我  19865890190

关闭

关闭

手机APP下载