建筑层高30米选择那种火灾探测器

层高30米可以选择线型光束感烟火灾探测吗,如果不可以应该选择那种探测器?


规范:12.4.3 线型光束感烟火灾探测器的设置应符合下列要求:
    1 探测器应设置在建筑顶部。
    2 探测器宜采用分层组网的探测方式。
    3 建筑高度不超过16m时,宜在6m~7m增设一层探测器。
    4 建筑高度超过16m但不超过26m时,宜在6m~7m和11m~12m处各增设一层探测器。


思劳 | 2024-08-28 11:41
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

张治福 2024-08-28 17:53 00 [回复]举报

火焰探测

思劳   回复: 张治福2024-08-29 09:15

这个厂房是煤仓,会有很多灰尘,可以使用这种吗。

符合下列条件之一的场所,不宜选择点型火焰探测器和图像型火焰探测器:
    1 在火焰出现前有浓烟扩散。
    2 探测器的镜头易被污染。
    3 探测器的“视线”易被油雾、烟雾、水雾和冰雪遮挡。
    4 探测区域内的可燃物是金属和无机物。
    5 探测器易受阳光、白炽灯等光源直接或间接照射。

0    0 [回复]举报

张治福   回复: 思劳2024-08-29 10:00

有点难搞哦,灰尘很重的场所,又是高大空间,光束感烟也不适用、火焰探测也不适用、感烟探测器也不适用、感温探测器又受高度限制。

0    0 [回复]举报

远方 2024-08-29 16:07 00 [回复]举报

    可以考虑使用图像型火灾探测器