使用蓄光型疏散指示地贴符合规范要求吗?什么场景可以使用?

使用蓄光型疏散指示地贴符合规范要求吗?什么场景可以使用?

ShiLiHui | 2024-08-28 22:13
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

花生12138 2024-08-29 11:22 20 [回复]举报

一般来说不能用蓄光型指示标志,消防应急照明和疏散指示系统技术标准 GB51309-2018规定,3.2.1 灯具的选择应符合下列规定:2 不应采用蓄光型指示标志替代消防应急标志灯具(以下简称“标志灯”)。有些场所,除了墙上要有指示标志之外,地面上也要设置,这种情况地面上的指示标志可以用蓄光型也可以用持续型。建筑设计防火规范 GB50016-2014(2018年版)规定,10.3.6 下列建筑或场所应在疏散走道和主要疏散路径的地面上增设能保持视觉连续的灯光疏散指示标志或蓄光疏散指示标志:     1 总建筑面积大于8000m²的展览建筑;     2 总建筑面积大于5000m²的地上商店;     3 总建筑面积大于500m²的地下或半地下商店;     4 歌舞娱乐放映游艺场所;     5 座位数超过1500个的电影院、剧场,座位数超过3000个的体育馆、会堂或礼堂;     6 车站、码头建筑和民用机场航站楼中建筑面积大于3000m²的候车、候船厅和航站楼的公共区。

我头发贼黑 2024-08-29 11:40 00 [回复]举报

在原有疏散指示标志符合规范的情况下,另行增添,哪里都可以使用;仅单独使用蓄光型的话,看建规10.3.6。

南明离火 2024-08-29 14:13 00 [回复]举报

如果是规范有要求做地面疏散指示的场所,那必须用灯光型;如果是规范没要求的场所,那随便