地下1层商业部分的疏散距离

一类高层公共建筑,地上25层地下2层,地下一层为商业,地下2层为汽车库,地下一层任一点至最近的安全出口的安全疏散距离怎样确定?

永锅 | 2023-03-17 09:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

秘密1 2023-03-17 12:00 10 [回复]举报

应分为两个方面确定,直通疏散走道的疏散门至安全出口的距离+房间内任一点至疏散门的距离;根据《建筑设计防火规范》GB50016-2014(2018版)5.5.17规定,其他高层建筑,位于两个安全疏散门之间直通疏散走道的门至最近安全出口的距离不应大于40米,位于袋型走道两侧的疏散门距离最近安全出口距离不应大于20米,若安装有自动喷水灭火系统,其距离可增加25%;至于房间内任一点至房间疏散门的直线距离同时不应大于上述相应形式的规定,若安装有自动喷水灭火系统,其距离可增加25%;还有一种情况是营业厅设置了2个疏散门,这时室内任一点距离疏散门距离不应大于30米,若安装了自动喷水灭火系统,其距离可增加25%,30乘25%=7.5米,最终室内任一点距离疏散门不应大于30+7.5=37.5米。

永锅   回复: 秘密12023-03-17 12:08

感谢您的回复,我问的是地下部分是商业功能的疏散,没找到相关的规范依据。

0    0 [回复]举报

张牙舞爪的张 2023-03-17 12:19 00 [回复]举报

判断地下一层场所类型如属于大商一部分可以参照大商管理规定的标准;如若不是,这种大型场所一般属于人防工程,可以查看人防工程规范。

消防网友73006 2023-03-19 12:39 10 [回复]举报

参照大商30米,设置自喷增加25%且行走距离不应超过45米

GG 2023-03-20 10:57 00 [回复]举报

安装了自动喷水灭火系统37.5米,没安装为30米。